Forums

We want to share an important update with our Betfair Community users.

Over the coming months, the Betfair Community platform will be winding down. The final active day for the platform will be December 21st. From December 22nd, users will no longer be able to access the platform.

Your discussions, insights, engagement, and, most importantly, feedback have helped shape the platform and guided innovation. Your feedback continues to be important to us, and we will continue to listen via our dedicated feedback channels, as well as through product testing and innovations.

To share your feedback and experience, visit: https://support.betfair.com/app/home

There is currently 1 person viewing this thread.
mexicano
11 Jan 10 14:21
Joined:
Date Joined: 13 Jan 02
| Topic/replies: 11,616 | Blogger: mexicano's blog
anybody able to tell me why my boiler keeps cutting out/cutting in even though the water is not up to full temperature, and the heating is not on as high as we want?

it seems to cut out after about 5 minutes, then cut back in after another 5 , any ideas?

thanks in advance .

Post your reply

Text Format: Table: Smilies:
Forum does not support HTML
Insert Photo
Cancel
sort by:
Show
per page
Replies: 8
By:
Reyes
When: 11 Jan 10 14:23
one main thermostat on wall? if so, where?
By:
mexicano
When: 11 Jan 10 14:30
in the hall.

but when the boiler cuts out there's still a fair way to go before it "clicks". if you know what i mean.
By:
BIG GURU
When: 11 Jan 10 15:06
Could be an airlock,what type of boiler and how old?
By:
Oxford Boy
When: 11 Jan 10 15:28
my guess is the pump is stuck/not circulating properly.
Boiler is cutting out on overheat stat. NAP
By:
iamajambo
When: 11 Jan 10 15:28
I had a new boiler installed last Febuary.Around about the beginning of December,before it got really cold, it developed a fault.Coming on from cold in the morning it would run for about 35-40.Thereafter,it would keep cutting in and out as it cooled.The thermister was faulty.Does this 'ring any bells'?

Now that it's really cold outside,the boiler is unable to cope with the demands being placed upon it and we are currently unable to achieve the requested temperature.Guess it's just not powerful enough for the size of our house or we need more radiators,which get too hot to touch for more than a second.The thing is,the boiler can only heat the circulating water so much and then it will turn itself off.This appears to be what's happening with mine.
By:
Oxford Boy
When: 11 Jan 10 16:09
You need to speak to the person who installed your boiler Jambo.
If that is true, your boiler is undersized, but my guess, is that the old system wasn't properly flushed.
By:
iamajambo
When: 11 Jan 10 17:24
Oxford,Are you knowledgable about these matters.The boiler is an Ideal Icos HE 24.It's in an ex -airing cupboard on the upper floor, so there were space constraints.We have a 4 bedroom semi.The upper floor rads heat up quickly,but one of the downstairs ones is slow to warm.Does this fit with your flushing theory ?
By:
Oxford Boy
When: 11 Jan 10 19:10
It's my living :)
24 KW boiler should comfortably heat 12 or more radiators. More inclined to think yours, as is original posters prob, is a circulation prob.
Blockage, stuck pump ?
Try turning valves off to all rads that get hot and see if one/ones that don't get hot, do start to get hot.
sort by:
Show
per page

Post your reply

Text Format: Table: Smilies:
Forum does not support HTML
Insert Photo
Cancel
‹ back to topics
www.betfair.com